model | Individual Ports |
|---|---|
USG FLEX 500H | P1, P2 |
USG FLEX 700H | P1, P2, P13, P14 |
ROLES | external | internal | general |
|---|---|---|---|
Characteristics | Ethernet VLAN Bridge LAG PPPoE | Ethernet VLAN Bridge LAG | Ethernet VLAN Bridge LAG |
Configurable Zone | Yes | Yes | Yes |
Static IP address | Yes | Yes | Yes |
DHCP client | Yes | No | Yes |
DHCP server/relay | No | Yes | Yes |
Default SNAT | Yes | No | No |
Packet size (MTU) | Yes | Yes | Yes |
Connectivity Check | Yes | Yes | Yes |
Interface | restriction | Required Port / Interface |
|---|---|---|
Ethernet interface | N/A | physical port |
LAG | When you configure a LAG interface, you cannot set the LAG interface on an Ethernet interface that is already used by other interfaces. | Ethernet interface |
Bridge interface | When you configure a bridge interface, you cannot set the bridge interface on an interface that is already used by other bridge or VLAN interfaces. | Ethernet interface* VLAN interface* |
Trunk | When you configure a trunk interface, you cannot set the trunk interface on an interface that is already used by other bridge or LAG interfaces. | External/General Ethernet interface VLAN interface LAG interface PPPoE interface bridge interface |
PPPoE interface | N/A | Ethernet interface* VLAN interface* bridge interface |
MAC Address | Port |
|---|---|
0A:0A:0A:0A:0A:0A | 2 |
MAC Address | Port |
|---|---|
0A:0A:0A:0A:0A:0A | 2 |
0B:0B:0B:0B:0B:0B | 4 |
IP Address(es) | Destination |
|---|---|
210.210.210.0/24 | lan1 |
210.211.1.0/24 | lan1:1 |
221.221.221.0/24 | vlan0 |
222.222.222.0/24 | vlan1 |
230.230.230.192/26 | wan2 |
241.241.241.241/32 | dmz |
242.242.242.242/32 | dmz |
IP Address(es) | Destination |
|---|---|
221.221.221.0/24 | vlan0 |
230.230.230.192/26 | wan2 |
241.241.241.241/32 | dmz |
242.242.242.242/32 | dmz |
250.250.250.0/23 | br0 |
IP Address(es) | Destination |
|---|---|
100.100.1.1/16 | lan1 |
200.200.200.1/24 | wan1 |
IP Address(es) | Destination |
|---|---|
0.0.0.0/0 | 200.200.200.100 |
Start IP Address | Pool Size | Range of Assigned IP Address |
|---|---|---|
50.50.50.33 | 5 | 50.50.50.33 - 50.50.50.37 |
75.75.75.1 | 200 | 75.75.75.1 - 75.75.75.200 |
99.99.1.1 | 1023 | 99.99.1.1 - 99.99.4.255 |
120.120.120.100 | 100 | 120.120.120.100 - 120.120.120.199 |



Label | Description |
|---|---|
External | |
Add | Click this to add a new entry. |
Edit | Select an entry and click Edit to open a screen where you can modify the entry’s settings. |
Remove | To remove a virtual interface, select it and click Remove. The Zyxel Device confirms you want to remove it before doing so. |
Reference | This field displays the objects this entry uses. |
Active | To turn on an entry, select it and click Active. The Status light changes accordingly. |
Inactive | To turn off an entry, select it and click Inactive. The Status light changes accordingly. |
Connect | To dial-up to a PPPoE interface, select it and click Connect. |
Disconnect | To disconnect from a PPPoE interface, select it and click Disconnect. |
Status | This icon is lit when the entry is active and dimmed when the entry is inactive. |
Name | This field displays the name of the interface. |
Zone | This displays the zone to which this interface belongs. An interface can only be in one zone. |
Description | This field displays the description of the interface. |
IP/Netmask | This field displays the current IP address, the subnet mask of the interface and whether the IP address is Static or dynamic (DHCP client). If this field is 0.0.0.0/0, the interface does not have an IP address yet. |
VLAN ID | This field displays the VLAN ID which is a 12-bit number that uniquely identifies each VLAN. |
Type | This field displays the interface type: Ethernet or VLAN. |
Ports | This field displays the port the interface is using. |
Reference | This field displays how many objects this entry uses. |
Internal | |
Add | Click this to add a new entry. |
Edit | Select an entry and click Edit to open a screen where you can modify the entry’s settings. |
Remove | To remove a virtual interface, select it and click Remove. The Zyxel Device confirms you want to remove it before doing so. |
Reference | This field displays the objects this entry uses. |
Active | To turn on an entry, select it and click Active. The Status light changes accordingly. |
Inactive | To turn off an entry, select it and click Inactive. The Status light changes accordingly. |
Status | This icon is lit when the entry is active and dimmed when the entry is inactive. |
Name | This field displays the name of the interface. |
Zone | This displays the zone to which this interface belongs. An interface can only be in one zone. |
Description | This field displays the description of the interface. |
IP/Netmask | This field displays the current IP address and the subnet mask of the interface. If this field is empty, the interface does not have an IP address yet. |
MAC Address | This field displays the MAC address of the interface hardwares. |
VLAN ID | This field displays the VLAN ID which is a 12-bit number that uniquely identifies each VLAN. |
Type | This field displays the interface type. |
Members | This field displays the port the interface is using. |
Reference | This field displays how many objects this entry uses. |
Advanced Settings | |
General | |
Add | Click this to add a new entry. |
Edit | Select an entry and click Edit to open a screen where you can modify the entry’s settings. |
Remove | To remove a general interface, select it and click Remove. The Zyxel Device confirms you want to remove it before doing so. |
Reference | This field displays the objects this entry uses. |
Active | To turn on an entry, select it and click Active. The Status light changes accordingly. |
Inactive | To turn off an entry, select it and click Inactive. The Status light changes accordingly. |
Status | This icon is lit when the entry is active and dimmed when the entry is inactive. |
Name | This field displays the name of the interface. |
Zone | This displays the zone to which this interface belongs. An interface can only be in one zone. |
Description | This field displays the description of the interface. |
IP/Netmask | This field displays the current IP address and the subnet mask of the interface. If this field is empty, the interface does not have an IP address yet. |
VLAN ID | This field displays the VLAN ID which is a 12-bit number that uniquely identifies each VLAN. |
Type | This field displays the interface type. |
Members | This field displays the Ethernet interfaces and VLAN interfaces in the bridge interface. It is blank for virtual interfaces. |
Reference | This field displays how many objects this entry uses. |
VTI | |
Edit | Select an entry and click Edit to open a screen where you can modify the entry’s settings. |
Remove | To remove a virtual interface, select it and click Remove. The Zyxel Device confirms you want to remove it before doing so. |
Reference | This field displays the objects this entry uses. |
Active | To turn on an entry, select it and click Active. The Status light changes accordingly. |
Inactive | To turn off an entry, select it and click Inactive. The Status light changes accordingly. |
Status | This icon is lit when the entry is active and dimmed when the entry is inactive. |
Name | This field displays the name of the interface. |
Zone | This displays the zone to which this interface belongs. An interface can only be in one zone. |
Label | Description |
|---|---|
General Settings | |
Enable Interface | Select this to enable this interface. Clear this to disable this interface. |
Interface Properties | |
Role | External is for connecting to an external network (like the Internet). The Zyxel Device automatically adds this interface to the default WAN trunk. |
Interface Type | Select the type of interface you want to configure. • Select Ethernet to establish the foundation for defining other interfaces and network policies. • Select VLAN to receive and send tagged frames. The Zyxel Device automatically adds or removes the tags as needed. • Select Bridge to create a single network between Ethernet or VLAN interfaces at the layer-2 (data link, MAC address) level. Unlike port groups, bridge interfaces can take advantage of some security features in the Zyxel Device, such as Policy Control and IP Exception. You can also assign an IP address and subnet mask to the bridge. • Select LAG to combine multiple ports into a single logical interface to increase bandwidth and provide redundancy. |
Name | Specify a name for the interface. It can use alphanumeric characters, hyphens, and underscores, and it can be up to 11 characters long. |
Port | This is the name of the Ethernet interface’s physical port. |
Member | This field displays when you select the VLAN Interface Type. Select the Ethernet interface on which the VLAN interface runs. |
Zone | Select the zone to which this interface is to belong. You use zones to apply security settings such as security policy, IPS, remote management, anti-malware, and application patrol. Make sure to select the correct zone as otherwise traffic may be blocked by a security policy. |
MAC Address | Have the interface use either the factory assigned default MAC address, a manually specified MAC address, or clone the MAC address of another device or computer. |
Use Default MAC Address | Select this option to have the interface use the factory assigned default MAC address. By default, the Zyxel Device uses the factory assigned MAC address to identify itself. |
Overwrite Default MAC Address | Select this option to have the interface use a different MAC address. Enter a MAC address in the format "xx:xx:xx:xx:xx:xx" or "xx-xx-xx-xx-xx-xx". Once it is successfully configured, the address will be copied to the configuration file. It will not change unless you change the setting or upload a different configuration file. |
VLAN ID | This field displays when you select the VLAN Interface Type. Enter the VLAN ID. This 12-bit number uniquely identifies each VLAN. Allowed values are 1 - 4094. (0 and 4095 are reserved.) |
Priority (802.1P) | This field displays when you select the VLAN Interface Type. Type a number between 0 and 7 to set the priority for the outgoing traffic from this interface. The bigger the number, the higher the priority. |
Description | Enter a description of this interface. You can use alphanumeric and ()+/:=?!*#@$_%- characters, and it can be up to 60 characters long. Spaces are allowed, but the string can’t start with a space. |
Address Assignment | These IP address fields configure an IPv4 IP address on the specified interface. If you change this IP address on the interface, you may also need to change a related address object for the network connected to the interface. For example, if you use this screen to change the IP address of your LAN interface, you should also change the corresponding LAN subnet address object. |
Unassigned | Select this if you don’t want to specify an IPv4 address for this interface. |
Get Automatically (DHCP) | Select this to make the interface a DHCP client and automatically get the IP address, subnet mask, and gateway address from a DHCP server. |
Use Fixed IP Address | Select this if you want to specify the IP address, subnet mask, and gateway manually. • IP/Network Mask: You must enter the primary IP address to identify the WAN interface’s address for sending traffic with other network devices. • Gateway IP: Enter the IP address of the neighboring device through which this WAN connection will send traffic. |
Secondary IP | This is available when you select Use Fixed IP Address. An interface can be bound to three additional public IP addresses. You can assign these IP addresses to different servers on the same interface, enabling the servers to receive traffic using different IP addresses and ports. |
Add | Click this to bind up to three additional IP addresses to this interface. |
Remove | To remove a secondary IP address, select it and click Remove. The Zyxel Device confirms you want to remove it before doing so. |
IP/Netmask | Enter the secondary IP address and subnet mask to bind to this interface. |
Members | This is available when you select Bridge or LAG interface type. |
Add | Click this to add a new interface. You can add up to eight interfaces to per bridge interface. |
Remove | To remove an interface from the bridge interface, select it and click Remove. The Zyxel Device confirms you want to remove it before doing so. |
Members | Select an Ethernet interface or VLAN interface to add it to the bridge interface. An interface is not available in the following situations: • There is a virtual interface on top of it. • It is already used in a different bridge interface. • Each bridge interface can only have one VLAN interface. |
Zone | Select the zone to which this interface is to belong. You use zones to apply security settings such as security policy, IPS, remote management, anti-malware, and application patrol. Make sure to select the correct zone as otherwise traffic may be blocked by a security policy. |
LAG Configuration | |
Mode | Select a Mode for this LAG interface. Choices are as follows: • static: Traffic is distributed to multiple links. • active-backup: Only one member of the LAG interface is active. Another member becomes active only if the current active interface member fails. • lacp (802.3ad): IEEE 802.3ad Dynamic link aggregation. Link Aggregation Control Protocol (LACP) negotiates automatic combining of links and balances the traffic load across the LAG link by sending LACP packets to the directly connected device that also implements LACP. The members must have the same speed and duplex settings. |
Mii Monitoring Interval | Set the link check interval in milliseconds that the system polls the Media Independent Interface (MII) to get status. MII monitors the physical network connection, and this interval determines how often the Zyxel Device checks if a connection has failed or been reconnected, especially for LAG interfaces, ensuring that all aggregated links are functioning properly. |
Transmit Hash Policy | This field is available when you select static or lacp (802.3ad) mode. This field sets the algorithm for member selection according to the selected TCP/IP layer. • src-dst-ip-mac: Uses source and destination IP addresses and MAC addresses for load balancing. • src-dst-mac: Uses only source and destination MAC addresses for load balancing. |
Primary | In active-backup mode, select a member as the active member to transmit and receive network traffic. If the active member fails, the Zyxel Device will automatically switch to another member as the new active member to ensure continuous network connectivity. |
PPPoE | Select this for a dial-up connection according to the information from your ISP. The following fields appear in the Add PPPoE screen. |
Authentication Type | Select an authentication protocol for outgoing connection requests. • Chap: Your Zyxel Device accepts CHAP only. • PAP: Your Zyxel Device accepts PAP only. • MSCHAP: Your Zyxel Device accepts MSCHAP only. • MSCHAP-V2: Your Zyxel Device accepts MSCHAP-V2 only. |
User Name | Enter the user name give to you by your ISP. You can use up to 30 single-byte characters, including 0-9a-zA-Z@._- |
Password | Enter the password associated with the user name. You can use 4 to 63 single-byte characters, including 0-9a-zA-Z’(){}<>^‘+/:!*#@&=$\.~%,|;-” |
Retype | Retype the password you entered in the Password field to confirm. |
Service Name | Enter the service name from your service provider. PPPoE uses a service name to identify and reach the PPPoE server. You can use up to 30 single-byte characters, including 0-9a-zA-Z._- |
Compression | Select On to turn on stac compression. Select Off to turn of stac compression. Stac compression is data compression technique capable of compressing data by a factor of about four. |
User Idle Timeout | Enter the idle timeout in seconds that elapses before the router automatically disconnects from the PPPoE server. |
WAN IP | Enter the IP address of the WAN interface through which this connection will send traffic. |
Gateway IP | Enter the IP address of the router through which this WAN connection will send traffic. |
Connectivity Check | The interface can regularly check the connection to the gateway you specified to make sure it is still available. You specify how often the interface checks the connection, how long to wait for a response before the attempt is a failure, and how many consecutive failures are required before the Zyxel Device stops routing to the gateway. The Zyxel Device resumes routing to the gateway the first time the gateway passes the connectivity check. |
Enable | Select this to turn on the connection check. |
Method | Select the method that the gateway allows. • Select ICMP to have the Zyxel Device regularly ping the gateway you specify to make sure it is still available. • Select TCP to have the Zyxel Device regularly perform a TCP handshake with the gateway you specify to make sure it is still available. |
Period | Enter the number of seconds between connection check attempts (5-600 seconds). |
Timeout | Enter the number of seconds to wait for a response before the attempt is a failure (1-10 seconds). |
Attempt | Enter the number of consecutive failures before the Zyxel Device stops routing through the gateway. |
Source | Enter the IPv4 address that test packets will be sent from. • Leave this field blank to send test packets from this external interface’s IP address. • Enter an IPv4 address to send test packets from the specified gateway. If the Zyxel Device uses PPPoE for the WAN and your ISP gave you an IP address, enter that IP address to check the connectivity. |
Destination | Enter one or two gateways using either FQDNs or IP addresses to receive test packets. For example, you can check if your ISP’s gateway is reachable. You can enter an IPv4 address in one field and a FQDN in the other. For example, type “192.168.1.2” in the top filed and “www.zyxel.com” in the bottom field. |
Success Criteria | This field applies when you specify two FQDNs or IP addresses for the connectivity check. • Select Any if you want the check to pass if at least one of the gateway with the specified IP address or FQDN responds. • Select All if you want the check to pass only if both gateways with the specified IP address or FQDN respond. |
Advanced Settings | |
DHCP Option 60 | This field appears when Role is set to External. The setting you configure here will only work when Address Assignment is set to Get Automatically. DHCP Option 60 is used by the Zyxel Device for identification to the DHCP server using the VCI (Vendor Class Identifier) on the DHCP server. The Zyxel Device adds it in the initial DHCP discovery message that a DHCP client broadcasts in search of an IP address. The DHCP server can assign different IP addresses or options to clients with the specific VCI or reject the request from clients without the specific VCI. Type a string using up to 63 of these characters [a-zA-Z0-9!\"#$%&\'()*+,-./:;<=>?@\[]^_`{}] to identify this Zyxel Device to the DHCP server. For example, Zyxel-TW. |
MTU | This is the Maximum Transmission Unit. Type the maximum size of each data packet, in bytes, that can move through this interface. If a larger packet arrives, the Zyxel Device divides it into smaller fragments. Allowed values are 1280-1500. Usually, this value is 1500. |
Egress Bandwidth Control | Click the switch to the right to limit outgoing traffic on the interface. |
Egress Rate Limit | Enter the maximum traffic the Zyxel Device can send through the interface to the network in Kbps (Kilobits per second), Mbps (Megabits per second), or Gbps (Gigabits per second). Allowed values range from 1 Kbps to 10 Gbps. If you also set an Upload Limit under Network > BWM, the Zyxel Device will apply the lower value as the limit. |
Ingress Bandwidth Control | Click the switch to the right to limit incoming traffic on the interface. |
Ingress Rate Limit | Enter the maximum traffic the Zyxel Device can receive from the network through the interface in Kbps (Kilobits per second), Mbps (Megabits per second), or Gbps (Gigabits per second). Allowed values range from 1 Kbps to 10 Gbps. If you also set a Download Limit under Network > BWM, the Zyxel Device will apply the lower value as the limit. |
Default SNAT | This field appears when Role is set to External. Select this to have the Zyxel Device use the IP address of the outgoing interface as the source IP address of the packets it sends out through its WAN trunks. The Zyxel Device automatically adds SNAT settings for traffic it routes from internal interfaces to external interfaces. |
Change to a Different ISP | If the Zyxel Device disconnects from the NCC (Nebula Control Center) after applying a WAN configuration change, it will revert to the last valid local WAN setting. Select this if you want to temporarily disable reverting to the last valid local WAN setting. |
Apply | Click Apply to save your changes back to the Zyxel Device. |
Cancel | Click Cancel to return the screen to its last-saved settings. |
Label | Description |
|---|---|
General Settings | |
Enable Interface | Select this to enable this interface. Clear this to disable this interface. |
Interface Properties | |
Role | Internal is for connecting to a local network. Other corresponding configuration options: DHCP server and DHCP relay. The Zyxel Device automatically adds default SNAT settings for traffic flowing from this interface to an external interface; for example LAN to WAN traffic. |
Interface Type | Select the type of interface you want to configure. • Select Ethernet to establish the foundation for defining other interfaces and network policies. • Select VLAN to receive and send tagged frames. The Zyxel Device automatically adds or removes the tags as needed. • Select Bridge to create a single network between Ethernet or VLAN interfaces at the layer-2 (data link, MAC address) level. Unlike port groups, bridge interfaces can take advantage of some security features in the Zyxel Device, such as Policy Control and IP Exception. You can also assign an IP address and subnet mask to the bridge. • Select LAG to combine multiple ports into a single logical interface to increase bandwidth and provide redundancy. |
Name | Specify a name for the interface. It can use alphanumeric characters, hyphens, and underscores, and it can be up to 11 characters long. |
Port | This is the name of the Ethernet interface’s physical port. |
Zone | Select the zone to which this interface is to belong. You use zones to apply security settings such as security policy, IPS, remote management, anti-malware, and application patrol. Make sure to select the correct zone as otherwise traffic may be blocked by a security policy. |
MAC Address | This field is read-only. This is the MAC address that the Ethernet interface uses. |
Description | Enter a description of this interface. You can use alphanumeric and ()+/:=?!*#@$_%- characters, and it can be up to 60 characters long. Spaces are allowed, but the string can’t start with a space. |
IPv4 Address Assignment | These IP address fields configure an IPv4 IP address on the interface itself. If you change this IP address on the interface, you may also need to change a related address object for the network connected to the interface. For example, if you use this screen to change the IP address of your LAN interface, you should also change the corresponding LAN subnet address object. |
Unassigned | Select this if you don’t want to specify an IP address for this interface. |
Use Fixed IP Address | Select this if you want to specify the IP address and subnet mask manually. |
Secondary IP | This is available when you select Use Fixed IP Address. An interface can be bound to three additional public IP addresses. You can assign these IP addresses to different servers on the same interface, enabling the servers to receive traffic using different IP addresses and ports. |
Add | Click this to bind up to three additional IP addresses to this interface. |
Remove | To remove a secondary IP address, select it and click Remove. The Zyxel Device confirms you want to remove it before doing so. |
IP/Netmask | Enter the secondary IP address and subnet mask to bind to this interface. |
Members | This is available when you select Bridge interface type. |
Add | Click this to add a new interface. You can add up to eight interfaces to per bridge interface. |
Remove | To remove an interface from the bridge interface, select it and click Remove. The Zyxel Device confirms you want to remove it before doing so. |
Members | Select an Ethernet interface or VLAN interface to add it to the bridge interface. An interface is not available in the following situations: • There is a virtual interface on top of it • It is already used in a different bridge interface • Each bridge interface can only have one VLAN interface. |
Zone | Select the zone to which this interface is to belong. You use zones to apply security settings such as security policy, IPS, remote management, anti-malware, and application patrol. Make sure to select the correct zone as otherwise traffic may be blocked by a security policy. |
LAG Configuration | |
Mode | Select a Mode for this LAG interface. Choices are as follows: • static: Traffic is distributed to multiple links. • active-backup: Only one member of the LAG interface is active. Another member becomes active only if the current active interface member fails. • lacp (802.3ad): IEEE 802.3ad Dynamic link aggregation. Link Aggregation Control Protocol (LACP) negotiates automatic combining of links and balances the traffic load across the LAG link by sending LACP packets to the directly connected device that also implements LACP. The members must have the same speed and duplex settings. |
Mii Monitoring Interval | Set the link check interval in milliseconds that the system polls the Media Independent Interface (MII) to get status. MII monitors the physical network connection, and this interval determines how often the Zyxel Device checks if a connection has failed or been reconnected, especially for LAG interfaces, ensuring that all aggregated links are functioning properly. |
Transmit Hash Policy | This field is available when you select static or lacp (802.3ad) mode. This field sets the algorithm for member selection according to the selected TCP/IP layer. • src-dst-ip-mac: Uses source and destination IP addresses and MAC addresses for load balancing. • src-dst-mac: Uses only source and destination MAC addresses for load balancing. |
Primary | In active-backup mode, select a member as the active member to transmit and receive network traffic. If the active member fails, the Zyxel Device will automatically switch to another member as the new active member to ensure continuous network connectivity. |
DHCP Server | This option appears when Address Assignment is Use Fixed IP Address. |
Enable | Select this to enable the DHCP server on the Zyxel Device. |
Mode | Select what type of DHCP service the Zyxel Device provides to the network. Choices are: • DHCP - the Zyxel Device assigns IP addresses and provides subnet mask, gateway, and DNS server information to the network. The Zyxel Device is the DHCP server for the network. • Relay - the Zyxel Device routes DHCP requests to one or more DHCP servers you specify. The DHCP server(s) may be on another network. You can have at most four DHCP relay servers at the same time. |
Start IP | Enter the IP address from which the Zyxel Device begins allocating IP addresses. If you want to assign a static IP address to a specific computer, use the Static DHCP Table. If this field is blank, the Pool Size must also be blank. In this case, the Zyxel Device can assign every IP address allowed by the interface’s IP address and subnet mask, except for the first address (network address), last address (broadcast address) and the interface’s IP address. |
Pool Size | Enter the number of IP addresses to allocate. This number must be at least one and is limited by the interface’s Subnet Mask. For example, if the Subnet Mask is 255.255.255.0 and Start IP is 10.10.10.10, the Zyxel Device can allocate 10.10.10.10 to 10.10.10.254, or 245 IP addresses. If this field is blank, the Start IP must also be blank. In this case, the Zyxel Device can assign every IP address allowed by the interface’s IP address and subnet mask, except for the first address (network address), last address (broadcast address) and the interface’s IP address. |
First DNS Server Second DNS Server Third DNS Server | Specify the IP addresses up to three DNS servers for the DHCP clients to use. Use one of the following ways to specify these IP addresses. • Custom Defined - enter a static IP address. • ZyWALL - the DHCP clients use the IP address of this interface and the Zyxel Device works as a DNS relay. |
First WINS Server Second WINS Server | Type the IP address of the WINS (Windows Internet Naming Service) server that you want to send to the DHCP clients. The WINS server keeps a mapping table of the computer names on your network and the IP addresses that they are currently using. |
Default Router | If you set this interface to DHCP Server, you can select to use either the interface’s IP address or another IP address as the default router. This default router will become the DHCP clients’ default gateway. To use another IP address as the default router, select Custom Defined and enter the IP address. |
Lease Time | Specify how long each computer can use the information (especially the IP address) before it has to request the information again. |
Static DHCP Table | Click this link to go to Network Status > DHCP Table to see the current DHCP-assigned IP addresses on an interface. |
DHCP Extended Options | This table is available if you selected DHCP server. Configure this table if you want to send more information to DHCP clients through DHCP packets. |
Add | Click this to create an entry in this table. See General Interface. |
Edit | Select an entry in this table and click this to modify it. |
Remove | Select an entry in this table and click this to delete it. |
PXE Server | PXE (Preboot eXecution Environment) allows a client computer to use the network to boot up and install an operating system via a PXE-capable Network Interface Card (NIC). PXE is available for computers on internal interfaces to allow them to boot up using boot software on a PXE server. The Zyxel Device acts as an intermediary between the PXE server and the computers that need boot software. The PXE server must have a public IPv4 address. You must enable DHCP Server on the Zyxel Device so that it can receive information from the PXE server. |
PXE Boot Loader File | A boot loader is a computer program that loads the operating system for the computer. Type the exact file name of the boot loader software file, including filename extension, that is on the PXE server. If the wrong filename is typed, then the client computers cannot boot. |
Relay Server 1 | |
Address | Enter the IP address of a DHCP server for the network. |
Upstream Interface | This field is optional. Select up to two interface(s)to use for the Zyxel Device to forward/receive DHCP packets to/from the DHCP server. |
Relay Server 2 | |
Address | This field is optional. Enter the IP address of another DHCP server for the network. |
Upstream Interface | This field is optional. Select up to two interface(s)to use for the Zyxel Device to forward/receive DHCP packets to/from the DHCP server. |
Advanced Settings | |
Connectivity Check | The interface can regularly check the connection to the gateway you specified to make sure it is still available. You specify how often the interface checks the connection, how long to wait for a response before the attempt is a failure, and how many consecutive failures are required before the Zyxel Device stops routing to the gateway. The Zyxel Device resumes routing to the gateway the first time the gateway passes the connectivity check. |
Enable | Select this to turn on the connection check. |
Method | Select the method that the gateway allows. • Select ICMP to have the Zyxel Device regularly ping the gateway you specify to make sure it is still available. • Select TCP to have the Zyxel Device regularly perform a TCP handshake with the gateway you specify to make sure it is still available. |
Period | Enter the number of seconds between connection check attempts (5-600 seconds). |
Timeout | Enter the number of seconds to wait for a response before the attempt is a failure (1-10 seconds). |
Attempt | Enter the number of consecutive failures before the Zyxel Device stops routing through the gateway. |
Source | Enter the IPv4 address that test packets will be sent from. • Leave this field blank to send test packets from this internal interface’s primary IP address, as configured above in Address Assignment. • Enter an IPv4 address to send test packets from the specified gateway. For example, you can enter a secondary IP address of this internal interface to check the connectivity. |
Destination | Enter one or two gateways using either FQDNs or IP addresses to receive test packets. For example, you can check if a device (for example, a router) or a server (for example, a DNS server) is reachable. You can enter an IPv4 address in one field and a FQDN in the other. For example, type “192.168.1.2” in the first field and “www.zyxel.com” in the second field. |
Success Criteria | This field applies when you specify two FQDNs or IP addresses for the connectivity check. • Select Any if you want the check to pass if at least one of the gateway with the specified IP address or FQDN responds. • Select All if you want the check to pass only if both gateways with the specified IP address or FQDN respond. |
Interface Parameters | |
MTU | This is the Maximum Transmission Unit. Type the maximum size of each data packet, in bytes, that can move through this interface. If a larger packet arrives, the Zyxel Device divides it into smaller fragments. Allowed values are 1280-1500. Usually, this value is 1500. |
Egress Bandwidth Control | Click the switch to the right to limit outgoing traffic on the interface. |
Egress Rate Limit | Enter the maximum traffic the Zyxel Device can send through the interface to the network in Kbps (Kilobits per second), Mbps (Megabits per second), or Gbps (Gigabits per second). Allowed values range from 1 Kbps to 10 Gbps. If you also set an Upload Limit under Interfaces > BWM, the Zyxel Device will apply the lower value as the limit. |
Ingress Bandwidth Control | Click the switch to the right to limit incoming traffic on the interface. |
Ingress Rate Limit | Enter the maximum traffic the Zyxel Device can receive from the network through the interface in Kbps (Kilobits per second), Mbps (Megabits per second), or Gbps (Gigabits per second). Allowed values range from 1 Kbps to 10 Gbps. If you also set a Download Limit under Interfaces > BWM, the Zyxel Device will apply the lower value as the limit. |
Apply | Click Apply to save your changes back to the Zyxel Device. |
Cancel | Click Cancel to return the screen to its last-saved settings. |
Label | Description |
|---|---|
General Settings | |
Enable Interface | Select this to enable this interface. Clear this to disable this interface. |
Interface Properties | |
Role | General is for connecting to either an external network or a local network. The rest of the screen’s options do not automatically adjust and you must manually configure a policy route to add routing and SNAT settings for the interface. |
Interface Type | Select the type of interface you want to configure. • Select Ethernet to establish the foundation for defining other interfaces and network policies. • Select VLAN to create an interface over an Ethernet interface that can receive and send tagged frames. The Zyxel Device automatically adds or removes the tags as needed. • Select Bridge to create a single network between Ethernet or VLAN interfaces at the layer-2 (data link, MAC address) level. Unlike port groups, bridge interfaces can take advantage of some security features in the Zyxel Device, such as Policy Control and IP Exception. You can also assign an IP address and subnet mask to the bridge. • Select LAG to combine multiple ports into a single logical interface to increase bandwidth and provide redundancy. |
Name | Specify a name for the interface. It can use alphanumeric characters, hyphens, and underscores, and it can be up to 11 characters long. |
Port | This is the name of the Ethernet interface’s physical port. |
Zone | Select the zone to which this interface is to belong. You use zones to apply security settings such as security policy, IPS, remote management, anti-malware, and application patrol. Make sure to select the correct zone as otherwise traffic may be blocked by a security policy. You can create a zone object in the Object > Zone screen. |
MAC Address | Have the interface use either the factory assigned default MAC address, a manually specified MAC address, or clone the MAC address of another device or computer. |
Use Default MAC Address | Select this option to have the interface use the factory assigned default MAC address. By default, the Zyxel Device uses the factory assigned MAC address to identify itself. |
Overwrite Default MAC Address | Select this option to have the interface use a different MAC address. Enter a MAC address in the format "xx:xx:xx:xx:xx:xx" or "xx-xx-xx-xx-xx-xx". Once it is successfully configured, the address will be copied to the configuration file. It will not change unless you change the setting or upload a different configuration file. |
VLAN ID | This field displays when you select the VLAN Interface Type. Enter the VLAN ID. This 12-bit number uniquely identifies each VLAN. Allowed values are 1 - 4094. (0 and 4095 are reserved.) |
Priority (802.1P) | This field displays when you select the VLAN Interface Type. Type a number between 0 and 7 to set the priority for the outgoing traffic from this interface. The bigger the number, the higher the priority. |
Description | Enter a description of this interface. You can use alphanumeric and ()+/:=?!*#@$_%- characters, and it can be up to 60 characters long. Spaces are allowed, but the string can’t start with a space. |
Address Assignment | These IP address fields configure an IPv4 IP address on the interface itself. If you change this IP address on the interface, you may also need to change a related address object for the network connected to the interface. For example, if you use this screen to change the IP address of your LAN interface, you should also change the corresponding LAN subnet address object. |
Unassigned | Select this if you don’t want to specify an IP address for this interface. |
Get Automatically (DHCP) | Select this to make the interface a DHCP client and automatically get the IP address, subnet mask, and gateway address from a DHCP server. |
Use Fixed IP Address | Select this if you want to specify the IP address, subnet mask, and gateway manually. |
IP/Network Mask | This field is enabled if you select Use Fixed IP Address. Enter the IP address the subnet mask of this interface in dot decimal notation. The subnet mask indicates what part of the IP address is the same for all computers on the network.for this interface. |
Gateway IP | This field is enabled if you select Use Fixed IP Address. Enter the IP address of the gateway. The Zyxel Device sends packets to the gateway when it does not know how to route the packet to its destination. The gateway should be on the same network as the interface. |
Secondary IP | This is available when you select Use Fixed IP Address. An interface can be bound to three additional public IP addresses. You can assign these IP addresses to different servers on the same interface, enabling the servers to receive traffic using different IP addresses and ports. |
Add | Click this to bind up to three additional IP addresses to this interface. |
Remove | To remove a secondary IP address, select it and click Remove. The Zyxel Device confirms you want to remove it before doing so. |
IP/Netmask | Enter the secondary IP address and subnet mask to bind to this interface. |
Members | This is available when you select Bridge interface type. |
Add | Click this to add a new interface. You can add up to eight interfaces to per bridge interface. |
Remove | To remove an interface from the bridge interface, select it and click Remove. The Zyxel Device confirms you want to remove it before doing so. |
Members | Select an Ethernet interface or VLAN interface to add it to the bridge interface. An interface is not available in the following situations: • There is a virtual interface on top of it • It is already used in a different bridge interface • Each bridge interface can only have one VLAN interface. |
Zone | Select the zone to which this interface is to belong. You use zones to apply security settings such as security policy, IPS, remote management, anti-malware, and application patrol. Make sure to select the correct zone as otherwise traffic may be blocked by a security policy. |
LAG Configuration | |
Mode | Select a Mode for this LAG interface. Choices are as follows: • static: Traffic is distributed to multiple links. • active-backup: Only one member of the LAG interface is active. Another member becomes active only if the current active interface member fails. • lacp (802.3ad): IEEE 802.3ad Dynamic link aggregation. Link Aggregation Control Protocol (LACP) negotiates automatic combining of links and balances the traffic load across the LAG link by sending LACP packets to the directly connected device that also implements LACP. The members must have the same speed and duplex settings. |
Mii Monitoring Interval | Set the link check interval in milliseconds that the system polls the Media Independent Interface (MII) to get status. MII monitors the physical network connection, and this interval determines how often the Zyxel Device checks if a connection has failed or been reconnected, especially for LAG interfaces, ensuring that all aggregated links are functioning properly. |
Transmit Hash Policy | This field is available when you select static or lacp (802.3ad) mode. This field sets the algorithm for member selection according to the selected TCP/IP layer. • src-dst-ip-mac: Uses source and destination IP addresses and MAC addresses for load balancing. • src-dst-mac: Uses only source and destination MAC addresses for load balancing. |
Primary | In active-backup mode, select a member as the active member to transmit and receive network traffic. If the active member fails, the Zyxel Device will automatically switch to another member as the new active member to ensure continuous network connectivity. |
DHCP Server | This option appears when Address Assignment is Use Fixed IP Address. |
Enable | Select this to enable the DHCP server on the Zyxel Device. |
Mode | Select what type of DHCP service the Zyxel Device provides to the network. Choices are: • DHCP - the Zyxel Device assigns IP addresses and provides subnet mask, gateway, and DNS server information to the network. The Zyxel Device is the DHCP server for the network. • Relay - the Zyxel Device routes DHCP requests to one or more DHCP servers you specify. The DHCP server(s) may be on another network. You can have at most four DHCP relay servers at the same time. |
Start IP | Enter the IP address from which the Zyxel Device begins allocating IP addresses. If you want to assign a static IP address to a specific computer, use the Static DHCP Table. If this field is blank, the Pool Size must also be blank. In this case, the Zyxel Device can assign every IP address allowed by the interface’s IP address and subnet mask, except for the first address (network address), last address (broadcast address) and the interface’s IP address. |
Pool Size | Enter the number of IP addresses to allocate. This number must be at least one and is limited by the interface’s Subnet Mask. For example, if the Subnet Mask is 255.255.255.0 and Start IP is 10.10.10.10, the Zyxel Device can allocate 10.10.10.10 to 10.10.10.254, or 245 IP addresses. If this field is blank, the Start IP must also be blank. In this case, the Zyxel Device can assign every IP address allowed by the interface’s IP address and subnet mask, except for the first address (network address), last address (broadcast address) and the interface’s IP address. |
First DNS Server Second DNS Server Third DNS Server | Specify the IP addresses up to three DNS servers for the DHCP clients to use. Use one of the following ways to specify these IP addresses. • Custom Defined - enter a static IP address. • ZyWALL - the DHCP clients use the IP address of this interface and the Zyxel Device works as a DNS relay. |
First WINS Server Second WINS Server | Type the IP address of the WINS (Windows Internet Naming Service) server that you want to send to the DHCP clients. The WINS server keeps a mapping table of the computer names on your network and the IP addresses that they are currently using. |
Default Router | If you set this interface to DHCP Server, you can select to use either the interface’s IP address or another IP address as the default router. This default router will become the DHCP clients’ default gateway. To use another IP address as the default router, select Custom Defined and enter the IP address. |
Lease Time | Specify how long each computer can use the information (especially the IP address) before it has to request the information again. |
DHCP Extended Options | This table is available if you selected DHCP server. Configure this table if you want to send more information to DHCP clients through DHCP packets. |
Add | Click this to create an entry in this table. See General Interface. |
Edit | Select an entry in this table and click this to modify it. |
Remove | Select an entry in this table and click this to delete it. |
PXE Server | PXE (Preboot eXecution Environment) allows a client computer to use the network to boot up and install an operating system via a PXE-capable Network Interface Card (NIC). PXE is available for computers on internal interfaces to allow them to boot up using boot software on a PXE server. The Zyxel Device acts as an intermediary between the PXE server and the computers that need boot software. The PXE server must have a public IPv4 address. You must enable DHCP Server on the Zyxel Device so that it can receive information from the PXE server. |
PXE Boot Loader File | A boot loader is a computer program that loads the operating system for the computer. Type the exact file name of the boot loader software file, including filename extension, that is on the PXE server. If the wrong filename is typed, then the client computers cannot boot. |
Relay Server 1 | |
Address | Enter the IP address of a DHCP server for the network. |
Upstream Interface | This field is optional. Select up to two interface(s)to use for the Zyxel Device to forward/receive DHCP packets to/from the DHCP server. |
Relay Server 2 | |
Address | This field is optional. Enter the IP address of another DHCP server for the network. |
Upstream Interface | This field is optional. Select up to two interface(s)to use for the Zyxel Device to forward/receive DHCP packets to/from the DHCP server. |
Connectivity Check | The interface can regularly check the connection to the gateway you specified to make sure it is still available. You specify how often the interface checks the connection, how long to wait for a response before the attempt is a failure, and how many consecutive failures are required before the Zyxel Device stops routing to the gateway. The Zyxel Device resumes routing to the gateway the first time the gateway passes the connectivity check. |
Enable | Select this to turn on the connection check. |
Method | Select the method that the gateway allows. • Select ICMP to have the Zyxel Device regularly ping the gateway you specify to make sure it is still available. • Select TCP to have the Zyxel Device regularly perform a TCP handshake with the gateway you specify to make sure it is still available. |
Period | Enter the number of seconds between connection check attempts (5-600 seconds). |
Timeout | Enter the number of seconds to wait for a response before the attempt is a failure (1-10 seconds). |
Attempt | Enter the number of consecutive failures before the Zyxel Device stops routing through the gateway. |
Source | Enter the IPv4 address that test packets will be sent from. • Leave this field blank to send test packets from this interface’s primary IP address, as configured above in Address Assignment. • Enter an IPv4 address to send test packets from the specified gateway. For example, you can enter a secondary IP address of this interface to check the connectivity. |
Destination | Enter one or two gateways using either FQDNs or IP addresses to receive test packets. For example, you can check Internet connectivity by entering 8.8.8.8 to see if Google DNS is reachable. You can enter an IPv4 address in one field and a FQDN in the other. For example, type “192.168.1.2” in the top filed and “www.zyxel.com” in the bottom field. |
Success Criteria | This field applies when you specify two FQDNs or IP addresses for the connectivity check. • Select Any if you want the check to pass if at least one of the gateway with the specified IP address or FQDN responds. • Select All if you want the check to pass only if both gateways with the specified IP address or FQDN respond. |
Interface Parameter | |
MTU | This is the Maximum Transmission Unit. Type the maximum size of each data packet, in bytes, that can move through this interface. If a larger packet arrives, the Zyxel Device divides it into smaller fragments. Allowed values are 1280-1500. Usually, this value is 1500. |
Egress Bandwidth Control | Click the switch to the right to limit outgoing traffic on the interface. |
Egress Rate Limit | Enter the maximum traffic the Zyxel Device can send through the interface to the network in Kbps (Kilobits per second), Mbps (Megabits per second), or Gbps (Gigabits per second). Allowed values range from 1 Kbps to 10 Gbps. If you also set an Upload Limit under Interfaces > BWM, the Zyxel Device will apply the lower value as the limit. |
Ingress Bandwidth Control | Click the switch to the right to limit incoming traffic on the interface. |
Ingress Rate Limit | Enter the maximum traffic the Zyxel Device can receive from the network through the interface in Kbps (Kilobits per second), Mbps (Megabits per second), or Gbps (Gigabits per second). Allowed values range from 1 Kbps to 10 Gbps. If you also set a Download Limit under Interfaces > BWM, the Zyxel Device will apply the lower value as the limit. |
Change to a Different ISP | If the Zyxel Device disconnects from the Nebula Control Center, it will revert to the previous configuration. If you select this option, the Zyxel Device will not revert to the previous configuration when it loses connection to the NCC due to an ISP change. |
Apply | Click Apply to save your changes back to the Zyxel Device. |
Cancel | Click Cancel to return the screen to its last-saved settings. |
Label | Description |
|---|---|
Option | This field displays the name of the selected DHCP option. Select which DHCP option that you want to add in the DHCP packets sent through the interface. |
Code | This field displays the code number of the selected DHCP option. If you selected User Defined in the Option field, enter a number for the option. This field is mandatory. |
Type | This is the type of the selected DHCP option. If you selected User Defined in the Option field, select an appropriate type for the value that you will enter in the next field. Only advanced users should configure User Defined. |
Value | Enter the value for the selected DHCP option. For example, if you selected TFTP Server Name (66) and the type is TEXT, enter the DNS domain name of a TFTP server here. This field is mandatory. |
First IP Address, Second IP Address, Third IP Address | If you selected Time Server (4), NTP Server (41), SIP Server (120), CAPWAP AC (138), or TFTP Server (150), you have to enter at least one IP address of the corresponding servers in these fields. The servers should be listed in order of your preference. |
First Enterprise ID, Second Enterprise ID | If you selected VIVC (124) or VIVS (125), you have to enter at least one vendor’s 32-bit enterprise number in these fields. An enterprise number is a unique number that identifies a company. |
First Class, Second Class | If you selected VIVC (124), enter the details of the hardware configuration of the host on which the client is running, or of industry consortium compliance. |
First Information, Second Information | If you selected VIVS (125), enter additional information for the corresponding enterprise number in these fields. |
OK | Click this to close this screen and update the settings to the previous Edit screen. |
Cancel | Click Cancel to close the screen. |
Option Name | Code | Description |
|---|---|---|
Time Offset | 2 | This option specifies the offset of the client's subnet in seconds from Coordinated Universal Time (UTC). |
Time Server | 4 | This option specifies a list of Time servers available to the client. |
Domain Name | 15 | This option specifies the domain name that the client should use when resolving hostnames through the Domain Name System. |
Interface MTU | 26 | This option specifies the MTU (Maximum Transmission Unit) to use on this interface, with an available range of 68 to 65535 bytes for IPv4 packets. |
NTP Server | 42 | This option specifies a list of the NTP servers available to the client by IP address. |
Netbios Scope | 47 | This option specifies the NetBIOS over TCP/IP scope parameter for the client. |
DHCP Server Identifier | 54 | This option specifies the IP address of the DHCP server. |
TFTP Server Name | 66 | This option is used to identify a TFTP server when the “sname” field in the DHCP header has been used for DHCP options. The minimum length of the value is 1. |
Bootfile | 67 | This option is used to identify a bootfile when the “file” field in the DHCP header has been used for DHCP options. The minimum length of the value is 1. |
SIP Server | 120 | This option carries either an IPv4 address or a DNS domain name to be used by the SIP client to locate a SIP server. |
VIVC | 124 | Vendor-Identifying Vendor Class option A DHCP client may use this option to unambiguously identify the vendor that manufactured the hardware on which the client is running, the software in use, or an industry consortium to which the vendor belongs. |
VIVS | 125 | Vendor-Identifying Vendor-Specific option DHCP clients and servers may use this option to exchange vendor-specific information. |
CAPWAP AC | 138 | CAPWAP Access Controller addresses option The Control And Provisioning of Wireless Access Points Protocol allows a Wireless Termination Point (WTP) to use DHCP to discover the Access Controllers to which it is to connect. This option carries a list of IPv4 addresses indicating one or more CAPWAP ACs available to the WTP. |
TFTP Server | 150 | The option contains one or more IPv4 addresses that the client may use. The current use of this option is for downloading configuration from a VoIP server via TFTP; however, the option may be used for purposes other than contacting a VoIP configuration server. |
Label | Description |
|---|---|
General Settings | |
Enable Interface | Slide the switch to the right to enable VTI. |
Interface Properties | |
Interface Name | This field displays the name of the VPN tunnel interface. This field is read-only. |
VPN Rule | This field displays the scenario rule the VPN tunnel interface is using. |
Zone | Select a zone. Make sure that the zone you select does not have traffic blocked by a security feature such as a security policy. |
IP Address | Enter the IP address for this interface. |
Connectivity Check | The interface can regularly check the connection to the gateway you specified to make sure it is still available. You specify how often the interface checks the connection, how long to wait for a response before the attempt is a failure, and how many consecutive failures are required before the Zyxel Device stops routing to the gateway. The Zyxel Device resumes routing to the gateway the first time the gateway passes the connectivity check. |
Enable | Select this to turn on the connection check. |
Method | Select the method that the gateway allows. Select ICMP to have the Zyxel Device regularly ping the gateway you specify to make sure it is still available. Select TCP to have the Zyxel Device regularly perform a TCP handshake with the gateway you specify to make sure it is still available. |
Period | Enter the number of seconds between connection check attempts. |
Timeout | Enter the number of seconds to wait for a response before the attempt is a failure. |
Attempt | Enter the number of consecutive failures before the Zyxel Device stops routing through the gateway. |
Source | Enter the IPv4 address that test packets will be sent from. • Leave this field blank to send test packets from this VPN tunnel interface’s IP address. • Enter an IPv4 address to send test packets from the specified gateway. |
Destination | Enter one or two gateways using either FQDNs or IP addresses to receive test packets. For example, you can check if a remote router at another site connected through the VPN is reachable by this interface. You can enter an IPv4 address in one field and a domain name in the other. For example, type “192.168.1.2” in the top filed and “www.zyxel.com” in the bottom field. |
Success Criteria | This field applies when you specify two FQDNs or IP addresses for the connectivity check. • Select Any if you want the check to pass if at least one of the gateway with the specified IP address or FQDN responds. • Select All if you want the check to pass only if both gateways with the specified IP address or FQDN respond. |
MTU | This is the Maximum Transmission Unit. Type the maximum size of each data packet, in bytes, that can move through this interface. If a larger packet arrives, the Zyxel Device divides it into smaller fragments. Allowed values are 1280-1500. |
Egress Bandwidth Control | Click the switch to the right to limit outgoing traffic on the interface. |
Egress Rate Limit | Enter the maximum traffic the Zyxel Device can send through the interface to the network in Kbps (Kilobits per second), Mbps (Megabits per second), or Gbps (Gigabits per second). Allowed values range from 1 Kbps to 10 Gbps. If you also set an Upload Limit under Interfaces > BWM, the Zyxel Device will apply the lower value as the limit. |
Ingress Bandwidth Control | Click the switch to the right to limit incoming traffic on the interface. |
Ingress Rate Limit | Enter the maximum traffic the Zyxel Device can receive from the network through the interface in Kbps (Kilobits per second), Mbps (Megabits per second), or Gbps (Gigabits per second). Allowed values range from 1 Kbps to 10 Gbps. If you also set a Download Limit under Interfaces > BWM, the Zyxel Device will apply the lower value as the limit. |
OK | Click OK to save your changes back to the Zyxel Device. |
Cancel | Click Cancel to return the screen to its last-saved settings. |
label | description |
|---|---|
Trunk Selection | Select whether the Zyxel Device is to use the default system WAN trunk or one of the user configured WAN trunks as the default trunk for routing traffic from internal interfaces to external interfaces. |
Force Reconnect on Active WAN | The passive interface is used if the active interface fails. If the active interface comes back up again, enable this if you want the Zyxel Device to end all connections on the passive interface first before the trunk goes back to using the active interface. |
Add | Click this to create a new user-configured trunk. |
Edit | Double-click an entry or select it and click Edit to open a screen where you can modify the entry’s settings. |
Remove | To remove a user-configured trunk, select it and click Remove. The Zyxel Device confirms you want to remove it before doing so. |
Reference | This field displays the objects this entry uses. |
Name | This field displays the label that you specified to identify the trunk. |
Algorithm | This field displays the load balancing method the trunk is set to use. |
Members | This field displays the interfaces that belong to the trunk. |
Reference | This field displays which settings use the entry. |
Label | Description |
|---|---|
Name | This is read-only if you are editing an existing trunk. When adding a new trunk, enter a descriptive name for this trunk. The value in this field cannot exceed 11 characters. The valid characters are [a-z][A-Z][_-]. |
Load Balancing Algorithm | Select a load balancing method to use from the drop-down list box. • Select Weighted Round Robin to balance the traffic load between interfaces based on their respective weights. An interface with a larger weight gets more chances to transmit traffic than an interface with a smaller weight. For example, if the weight ratio of wan1 and wan2 interfaces is 2:1, the Zyxel Device chooses wan1 for 2 sessions’ traffic and wan2 for 1 session’s traffic in each round of 3 new sessions. • Select Least Load First to send new session traffic through the least utilized trunk member. • Select Spillover to send network traffic through the first interface in the group member list until there is enough traffic that the second interface needs to be used (and so on). |
Load Balancing Index(es) | This field is available if you selected to use the Least Load First or Spillover method. Select Outbound, Inbound, or Outbound + Inbound to set the traffic to which the Zyxel Device applies the load balancing method. Outbound means the traffic traveling from an internal interface (ex. LAN) to an external interface (ex. WAN). Inbound means the opposite. |
Add | Click this to create a WAN trunk entry. |
Edit | Select an entry and click Edit to modify the entry’s settings. |
Remove | To remove a member interface, select it and click Remove. The Zyxel Device confirms you want to remove it before doing so. |
Name | Select an interface name from the drop-down list box. |
Mode | Click this table cell. • Select Active to have the Zyxel Device always attempt to use this connection. • Select Passive to have the Zyxel Device only use this connection when all of the connections set to active are down. You can only set one of a group’s interfaces to passive mode. |
Parameter | This field displays with the weighted round robin load balancing algorithm. Specify the weight (1~10) for the interface. The weights of the different member interfaces form a ratio. This ratio determines how much traffic the Zyxel Device assigns to each member interface. The higher an interface’s weight is (relative to the weights of the interfaces), the more sessions that interface should handle. |
Apply | Click this button to save your changes to the Zyxel Device. |
Cancel | Click Cancel to return the screen to its last-saved settings. |
Label | Description |
|---|---|
Name | This field displays the name of the selected system default trunk. |
Load Balancing Setting | This field displays the load balancing method use for the default trunk. Weighted Round Robin (wrr) balances the traffic load between interfaces based on their respective weights. An interface with a larger weight gets more chances to transmit traffic than an interface with a smaller weight. For example, if the weight ratio of wan1 and wan2 interfaces is 2:1, the Zyxel Device chooses wan1 for 2 sessions’ traffic and wan2 for 1 session’s traffic in each round of 3 new sessions. |
The table lists the trunk’s member interfaces. This table is read-only. | |
Interface | This column displays the name of the member interfaces. |
Mode | This field displays Active if the Zyxel Device always attempt to use this connection. This field displays Passive if the Zyxel Device only use this connection when all of the connections set to active are down. Only one of a group’s interfaces can be set to passive mode. |
Parameter | This field displays with the weighted round robin load balancing algorithm. Specify the weight (1~10) for the interface. The weights of the different member interfaces form a ratio. |
Apply | Click Apply to save your changes to the Zyxel Device. |
Cancel | Click Cancel to return the screen to its last-saved settings. |
Label | Description |
|---|---|
Virtual Device | This shows which ports are up or down on the Zyxel Device. Hover over a port to see port details such as name, status , interface and IP address. |
Configuration | Select an entry to configure the speed negotiation setting of the Ethernet connection on this port and PoE if the port supports it. |
Name | This field displays the name of the port. |
Status | This field displays the speed and the duplex mode of the Ethernet connection on the port. |
Type | This field displays the cable type that is used on the port. |
Setting | Select the speed and the duplex mode of the Ethernet connection on this port. Choices are Auto Negotiate, 10Mbps, 100Mbps, 1Gbps and 2.5Gbps. Selecting Auto Negotiate allows one port to negotiate with a peer port automatically to obtain the connection speed (of up to 1000M) and duplex mode that both ends support. When auto-negotiation is turned on, a port on the Zyxel Device negotiates with the peer automatically to determine the connection speed and duplex mode. If the peer port does not support auto-negotiation or turns off this feature, the Zyxel Device determines the connection speed by detecting the signal on the cable and using half duplex mode. When the Zyxel Device’s auto-negotiation is turned off, a port uses the pre-configured speed and duplex mode when making a connection, thus requiring you to make sure that the settings of the peer port are the same in order to connect. To avoid errors, it is recommended to set both the Zyxel Device and the peer port to the same speed and duplex mode. For example: • Auto Negotiate—Auto Negotiate • 10Mbps—10Mbps • 100Mbps—100Mbps • 1Gbps—1Gbps • 2.5Gbps—2.5Gbps |
Interface | This field displays the interface for the port. |
PoE | If the port supports PoE, then this field displays if PoE is enabled on the port. |
Edit | Select an entry and click this icon to modify it. ![]() |
Remove | Select an entry and click this icon to delete it. ![]() |
Save Changes | Click this icon to save the changes in this row. ![]() |
Cancel Changes | Click this icon to cancel the changes in this row. ![]() |